This article is a follow-up to Comparing search head hardware changes and their impact on Splunk platform search performance, applying the same testing framework to a second Splunk platform search head cluster migration. Here, the destination servers are newer, but the search head cluster is much smaller and less busy, so the results and variance profile differ.

This article walks you through the scenario, showing the hardware differences, the performance findings for both scheduled and ad-hoc searches, and the reusable comparison framework, this time updated to also capture dashboard search performance.

The findings in this article reflect a specific hardware comparison carried out by the author, Gareth Anderson, in his own environment, so your results might vary depending on workload, hardware generation, firmware, OS configuration, and search head sizing. You should treat these results as a reference point and benchmark against your own environment before making procurement decisions.

The hardware differences

The servers old-004 to old-006 used throughout this article are the same "type" of CPU (base clock 2.70 Ghz, maximum turbo of 3.70 Ghz). Servers new-004 to new-006 are the newer type of hardware (base clock 3.60 Ghz, maximum turbo of 4.10 Ghz).

CPU configuration

The migration was occurring from the 2.70 Ghz to the 3.60 Ghz processors; only these two types of hardware were included to simplify the comparison.

The servers were not heavily utilized. The turbo clock speeds appeared to be around 4.0 Ghz on the new servers and as high as 3.4 Ghz on the old servers — either way, there is close to 20% more clock speed on the newer servers when both use turbo boost. The newer CPU also benefits from an approximately 6-year-newer generation of hardware. This image shows the CPU utilization across the old and new servers:

cpu-comparison-graph-14days.png

Overall the CPU utilization is very low. The newer servers have fewer total cores, so the higher utilization percentage is expected.

I/O performance

This image shows the disk read service times, measured using Nmon:

disk-read-service-times.png

This image shows the disk read IOPS:

disk-read-iops.png

Overall the read IOPS is extremely low; a lot of the data is likely sitting in the hundreds of gigabytes of memory available to the server.

This image shows the disk write service times:

disk-write-service-times.png

This image shows the disk write IOPS:

disk-write-iops.png

There is more write activity on the old servers. The new servers have newer NVMe drives, which appears to reduce the write latency.

This image shows the introspection data average I/O service times:

introspection-stats-disk-splunk.png

Overall the newer hardware is "faster" at both the I/O and CPU levels. With the low overall CPU utilization, both old and new servers can regularly use their turbo speed, confirmed at roughly 3.4 Ghz and 4.0 Ghz respectively.

Summary of findings

The following sections detail the differences between comparing scheduled searches versus ad-hoc search runs. This image shows the main findings for scheduled search runtimes—the average search head performance improvement over 7 days—broken down by runtime:

avg_shc_diff_by_runtime_no_ratio_7days.png

This image shows the average search head performance improvement over 30 days, broken down by runtime:

avg_shc_diff_by_runtime_no_ratio_30days.png.png

The improvement here is minimal. However, the graphs above do not isolate searches spending the majority of their time in phase 1, and the indexing tier is unchanged, so phase 0 should be roughly the same during the testing period. The difference is visible but much less than expected; a 2% average improvement seems quite low for the newer hardware combination.

If we change the ratio to less than 50% (so at least half of the overall search time is spent in phase 1), we see the following: the average search head performance improvement over 7 days, broken down by runtime, with longer phase 1 times:

avg_shc_diff_by_runtime_with_rati_7dayso.png

This image shows the average search head performance improvement over 30 days, broken down by runtime, with longer phase 1 times:

avg_shc_diff_by_runtime_with_ratio_30days.png

Looking over 30 days was expected to show a larger improvement, but it simply decreased the percentage, and in some cases produced a negative result (which might be attributable to chance).

Dashboard performance changes were also graphed, but there was not enough data in this environment to draw any conclusions. In an alternative environment, dashboards did tend to see a larger benefit than saved searches (closer to 20% in many cases, while the saved searches saw less than 5% improvement).

Performance changes by search type

This image shows the average search head improvement broken down by type of search over 7 days:

avg_shc_diff_by_search_type_7days.png

This image shows the average search head improvement broken down by type of search over 30 days:

avg_shc_diff_by_search_type_30days_no_ratio.png

The local searches show minimal benefit from the hardware change, while the mcatalog searches show close to 4% improvement. Either way, this is less than expected.

If we include the ratio and therefore check searches that spent at least an equal amount of time in phase 1 compared to phase 0, we see the following: the average search head improvement by type of search over 7 days, with longer phase 1 times:

shc_diff_by_search_type_with_ratio_7days.png

This image shows the average search head improvement by type of search over 30 days, with longer phase 1 times:

shc_diff_by_search_type_with_ratio_30days.png

Again, the average scheduled search had hardly changed. If we instead look at the 95th percentile, some saved searches are seeing larger improvements. This image shows the 95th percentile search head improvement broken down by runtime over 7 days:

perc95_by_runtime_noratio_7days.png

This image shows the 95th percentile search head improvement broken down by runtime over 30 days:

perc95_by_runtime_noratio_30days.png

Adding in the ratio should show further benefit, as these searches spend a longer time in phase 1 exclusively. This image shows the 95th percentile search head improvement broken down by range over 7 days, with longer phase 1 times:

perc95_runtime_with_ratio_7days.png

This image shows the 95th percentile search head improvement broken down by range over 30 days, with longer phase 1 times:

perc95_runtime_with_ratio_30days.png

If we change the breakdown to search type, we can see that the search and mstats commands receive the largest benefit. This image shows the 95th percentile search head improvement broken down by search type over 7 days:

perc95_by_search_type_noratio_7days.png

This image shows the 95th percentile search head improvement broken down by search type over 30 days:

perc95_by_search_type_noratio_30days.png

If we now include the ratio for longer phase 1 times, this image shows the 95th percentile search head improvement broken down by search type over 7 days, with longer phase 1 times:

perc95_shc_diff_with_ratio_7days_by_searchtype.png

This image shows the 95th percentile search head improvement broken down by search type over 30 days, with longer phase 1 times:

perc95_shc_diff_with_ratio_30days_by_searchtype.png

Overall, some searches are seeing a significant benefit and others are not. Some simple dashboard searches might show different results to the scheduled searches, but that testing was not run.

Variance between scheduled search runtimes

One difference from the previous search head cluster and article is the consistency between scheduled search runs. This image shows the average phase 0 variance between runs over 7 days:

phase0_distribution_over_7days.png

This image shows the average phase 0 variance between runs over 30 days:

phase0_distribution_over_30days.png

This image shows the average phase 0 variance between runs over 7 days, broken down by runtime:

avg_phase_0_variance_by_runtime_7days.png

This image shows the average phase 0 variance between runs over 30 days, broken down by runtime:

avg_phase_0_variance_by_runtime_30days.png

This image shows the average phase 1 variance between runs over 7 days, broken down by runtime:

avg_phase_1_variance_by_runtime_7days.png

This image shows the average phase 1 variance between runs over 30 days, broken down by runtime:

avg_phase_1_variance_by_runtime_30days.png

This image shows the average phase 1 variance between runs over 7 days:

phase1_dsitribution_7days.png

This image shows the average phase 1 variance between runs over 30 days:

phase1_distriution_30ays.png

The majority of searches on this cluster show a relatively close runtime between runs. In the previous test, there were results with around 30% variance between search runs, and quite a lot at 40% or more. In this environment, a lot of the searches were within 10% of their phase 1 runtime, with a little more variance from the indexing tier.

This image shows the average phase 0 variance by search type over 7 days:

avg_phase_0_variance_by_search_type_7days.png

This image shows the average phase 0 variance by search type over 30 days:

avg_phase_0_varaince_by_search_type_30days.png

This image shows the average phase 1 variance by search type over 7 days:

avg_phase_1_variance_by_search_type_7days.png

This image shows the average phase 1 variance by search type over 30 days:

avg_phase_1_variance_by_search-type_30days.png

In terms of gathering this data, the search was extremely slow:

  • 29,308 results by scanning 10,602,528 events in 1,256.504 seconds
  • 46,350 results by scanning 46,026,829 events in 5,705.176 seconds

For the 30 day search, auto-finalization kicked in due to reaching the disk quota, and the search had to be re-run. The search used to determine these results clearly requires optimization, but it is only intended for occasional use.

Results from ad-hoc testing

For ad-hoc testing, the following queries were run:

index=_internal earliest=-1m
index=_internal earliest=-10m | stats count BY host, source
index=_internal earliest=-60m | stats count BY host, source

This image shows a graph of the percentage improvement per type of ad-hoc search (all in Smart mode):

manal-results-percentage-comparison.png

The pure events search run in Smart mode returned a large volume of results and showed the largest improvement, close to a 50% decrease in runtime across the testing. This is likely helped by the faster I/O write performance. The stats-based queries showed less than 20% improvement, which is likely the CPU difference taking effect.

Updates to the testing method

The query has been updated to include dashboard performance this time, as dashboard performance appears to vary more (in this SHC) than the saved searches, and it is more noticeable to the userbase:

| multisearch 
    [ search index=_introspection sourcetype=search_telemetry `searchheadhosts` perf.search_runtime_secs>2 search_id!=1*
    | eval hour=strftime(_time, "%H"), minute=strftime(_time, "%M"), dayofweek=strftime(_time, "%a") 
    | rename desc.app AS app
    | fields phases.phase_0.elapsed_time_aggregations.max, phases.phase_1.elapsed_time_aggregations.max, host, search_id app ] 
    [ search index=_audit `searchheadhosts` info=completed total_run_time>2 search_id="'scheduler*" has_error_warn=false fully_completed_search=true 
    | eval hour=strftime(_time, "%H"), minute=strftime(_time, "%M"), dayofweek=strftime(_time, "%a") 
    | eval search_id=trim(search_id,"\'")
    | rex ", savedsearch_name=\"(?P<savedsearch_name>.*?)\", search_startup_time"
    | rex "(?s), search='(?P<search>.*)\]$" 
    | rex field=search mode=sed "s/\n/ /g" 
    | eval search=if(substr(search,len(search),len(search)-1)=="'",substr(search,0,len(search)-1),search)
    | rex field=search "^(\s*\|\s*)?\s*(?P<command>\S+)" 
    | rex field=search "(\||^)\s*(?P<subsearch>(append|union|multisearch|set|appendcols|appendpipe|join|map))"
    | eval subsearch=if(isnotnull(subsearch),"true","false")
    | eval search_type=case(command="ldapsearch" OR command="runaql" OR command="dbxquery","remote_server",command="tstats" OR command="metadata" OR command="eventcount","metadata",command="makeresults" OR command="inputlookup" OR command="rest" OR command="loadjob" OR command="noop" OR command="stats","local",match(command,"^trackme"),"customcommand",command="multisearch" OR command="union" OR command="savedsearch" OR command="datamodel" OR command="from" OR command="set","search",command="`","search",1=1,command)
    | eval search_source="savedsearch"
    | fields total_run_time, savedsearch_name, search_id, result_count, event_count, scan_count, search_type, app, subsearch, search_source ] 
    [ search index=_audit `searchheadhosts` info=completed total_run_time>2 has_error_warn=false fully_completed_search=true provenance="UI:Dashboard:*"
    | eval hour=strftime(_time, "%H"), minute=strftime(_time, "%M"), dayofweek=strftime(_time, "%a") 
    | eval search_id=trim(search_id,"\'")
    | eval time_period=round(api_lt-api_et) 
    | eval time_period = case(
        time_period >= 1296000, ceil(time_period/86400)*86400,
        time_period >= 14400 , ceil(time_period/60/60)*3600,
        time_period >= 300, ceil(time_period/60)*60,
        true(), time_period
        )     
    | eval time_period=if(api_et=="N/A","alltime",time_period)
    | rex ", savedsearch_name=\"(?P<savedsearch_name>.*?)\", search_startup_time"
    | eval savedsearch_name=provenance . "_" . savedsearch_name . "_" . time_period
    | rex "(?s), search='(?P<search>.*)\]$" 
    | rex field=search mode=sed "s/\n/ /g" 
    | eval search=if(substr(search,len(search),len(search)-1)=="'",substr(search,0,len(search)-1),search)
    | rex field=search "^(\s*\|\s*)?\s*(?P<command>\S+)" 
    | rex field=search "(\||^)\s*(?P<subsearch>(append|union|multisearch|set|appendcols|appendpipe|join|map))"
    | eval subsearch=if(isnotnull(subsearch),"true","false")
    | eval search_type=case(command="ldapsearch" OR command="runaql" OR command="dbxquery","remote_server",command="tstats" OR command="metadata" OR command="eventcount","metadata",command="makeresults" OR command="inputlookup" OR command="rest" OR command="loadjob" OR command="noop" OR command="stats","local",match(command,"^trackme"),"customcommand",command="multisearch" OR command="union" OR command="savedsearch" OR command="datamodel" OR command="from" OR command="set","search",command="`","search",1=1,command)
    | eval search_source="dashboard"
    | fields total_run_time, savedsearch_name, search_id, result_count, event_count, scan_count, search_type, app, subsearch, search_source ]
| eval type="new"
| selfjoin search_id app
| table _time, phases.phase_0.elapsed_time_aggregations.max, phases.phase_1.elapsed_time_aggregations.max, host, savedsearch_name, total_run_time, result_count, event_count, scan_count search_type app subsearch search_source
| bin _time span=24h 
| stats count, avg(phases.phase_1.elapsed_time_aggregations.max) AS avg_sh_time, avg(phases.phase_0.elapsed_time_aggregations.max) AS avg_indexer_time, avg(total_run_time) AS total_run_time, avg(scan_count) AS scan_count, avg(event_count) AS event_count, avg(result_count) AS result_count, values(subsearch) AS subsearch, stdev(phases.phase_1.elapsed_time_aggregations.max) AS phase_1_stdev, stdev(phases.phase_0.elapsed_time_aggregations.max) AS phase_0_stdev by savedsearch_name, type, _time, search_type, app, search_source
| eval phase_1_diff=round(phase_1_stdev/avg_sh_time,3), phase_0_diff=round(phase_0_stdev/avg_indexer_time,3)
| eventstats perc95(phase_1_diff) AS phase_1_diff, perc95(phase_0_perc) AS phase_0_diff, avg(phase_0_diff) AS avg_phase_0_diff, avg(phase_1_diff) AS avg_phase_1_diff by savedsearch_name, search_type, app
| eval day=strftime(_time, "%a") 
| eval hour=strftime(_time, "%H")
| sort 0 savedsearch_name type
| streamstats window=1 global=f current=f reset_on_change=true values(avg_sh_time) AS avg_new_sh_time, values(avg_indexer_time) AS avg_new_indexer_time, values(scan_count) AS prev_scan_count, values(event_count) AS prev_event_count, values(result_count) AS prev_result_count by savedsearch_name
| eval shc_diff=((avg_sh_time/avg_new_sh_time)-1)*100, indexer_diff=((avg_indexer_time/avg_new_indexer_time)-1)*100
| eval ratio=(100/avg_sh_time)*avg_indexer_time
| foreach avg* phase_* ratio shc_diff total_run_time [eval <<FIELD>>=round('<<FIELD>>',2)]
| rangemap field=avg_sh_time 1-3=1-3 4-6=4-6 7-10=7-10 11-30=11-30 31-60=31-60 61-120=61-120 121-300=121-300 301-600=301-600 default=over600

Conclusion

The expectations had already been adjusted after the previous test to expect a small difference. However, the combination of faster I/O and faster CPU was expected to make a more noticeable difference to performance.

While some searches did appear to have a 20% or greater benefit, the overall benefits in scheduled search performance were, on average, very small. The manual comparisons showed clear benefits for a simple query, but this does not translate to the saved searches.

Overall, the newer hardware does help improve performance, but the benefits for scheduled searches are minimal—even in this particular SHC, which has an extremely small user base of approximately 8 active users.

The previous article describes the testing methods and a more complicated comparison across other search head clusters.

Additional resources